  1. Reset the thermal cutout on the fan motor and allow the motor to cool.
  2. Check that the wiring is done according to the user manual.
  3. Use a test light or voltmeter to test the power at the control.
  4. Replace the fuse. If the fuse blows immediately, a problem exists with the wiring or the fan motor. If the fuse blows after a delay (minutes, days, or weeks), the load is exceeding the current rating of the control.